Since this is an international forum, I was hoping someone from the EU could help me decipher some transformer markings.

 

Transformer Label

 

Is this a 2.4KVA transformer or a 630VA transformer?  I've searched the web and I can't figure out what the PN and PK designations signify.

Cheers,

Tom

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

My guess: based on how it wires to source, Pn Phase to Neutral (star),  Pk Phase to phase (delta).

 

Jim

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

ki0bk wrote:
My guess: based on how it wires to source, Pn Phase to Neutral (star), Pk Phase to phase (delta).

 

Sorry, but this is almost certainly wrong.
P_N is  the nominal power and P_K is the short circuit power (K for Kurzschluss). So it's a 630 VA Transformer that can draw up to 2.3 kVA when it's shorted.
Verb. is short for Verbinden, meaning that these terminals should be connected together.
Anschl. is short for Anschluss, meaning that's where you connect the power source (probably the grid) or the load respectively.

"Some people die at 25 and aren't buried until 75." -Benjamin Franklin

 

What is life's greatest illusion?"  "Innocence, my brother." -Skyrim

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

tblough, could you maybe tell us what this transformer is used for? Is it an isolation transformer? Or is it used to adapt a specific load to different distribution grids? It's not usual for a transformer to have equal input and output voltages...

"Some people die at 25 and aren't buried until 75." -Benjamin Franklin

 

What is life's greatest illusion?"  "Innocence, my brother." -Skyrim

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Continuous/Peak VA?

If you can hold it in front of you with your arms extended, it might be 630VA

If you can't, it might be 2400 VA 8)

Tom Pappano
Tulsa, Oklahoma

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

I have no idea what it began life for, but I want to use it to power some DC servo motors.  I have 230V single phase input to the machine and I need something around 110-120VAC so it will be rectified below 180VDC.  I need about 20A of the 150VDC this should generate so , 20A * 115V means I need a 2.3-2.4KVA transformer.  I just cant tell if this is indeed a 2.4KVA transformer.

 

If you can hold it in front of you with your arms extended, it might be 630VA

If you can't, it might be 2400 VA 8)

It's an eBay auction so I can't physically lift the item ;-)

Cheers,

Tom

Last Edited: Mon. Feb 12, 2018 - 08:38 PM
  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Hope, this spec may be useful (part number matches)

http://www.mcttrafo.com/medien/2--steuertrafo_100_-_1000_va.pdf

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 1

tblough wrote:
I need a 2.3-2.4KVA transformer

 

Well then you shouldn't buy a transformer from Germany (or any other part of Europe). The price tag for shipping such a beast across the Atlantic might just give you a heart attack when you see it cheeky

"Some people die at 25 and aren't buried until 75." -Benjamin Franklin

 

What is life's greatest illusion?"  "Innocence, my brother." -Skyrim

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Vladivolt wrote:

Hope, this spec may be useful (part number matches)

http://www.mcttrafo.com/medien/2--steuertrafo_100_-_1000_va.pdf

 

The mixture of German and Greek is still too much for me ;-)  What do Power DB (cosφ=1) and Power DB (cosφ=0.5) signify?  Duty cycles?  However the dimensions do compare favorable to what we 'Muricans would call a 2.4KVA transformer.

 

Quote:

Well then you shouldn't buy a transformer from Germany (or any other part of Europe). The price tag for shipping such a beast across the Atlantic might just give you a heart attack when you see it cheeky

 

Luckily, it's currently located in South Carolina USA!  Even so, shipping is still a bear.

Cheers,

Tom

Last Edited: Mon. Feb 12, 2018 - 09:23 PM
  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

tblough wrote:
What do Power DB (cosφ=1) and Power DB (cosφ=0.5) signify?
.

 

I honestly can't answer what DB stands for. But φ (phi) is the angle between current and voltage. A transformer coil is a reactive load, so voltage and current are not in phase.
When the voltage is at it's peak, the current is still rising. And when the voltage crosses zero, the current is still flowing.
For an inductive load, the current lags behind the voltage( you need voltage to change the current) and for a capacitive load it's the opposite(you need current to change the voltage).
The delay is usually not given as time, but as an angle, with phi universally used as the symbol for that.
To make things worse even, cos(phi) is normally given, so you need to figure out yourself whether current leads or lags.

 

Now the consequence of voltage and current not being in phase is that the power can no longer be calculated  by multiplying the mean values of U and I. That would be called the apparent power S, measured in VA. The actually consumed power P is U*I*cos(phi), given in W. The "difference"(not as in Q=S-P)  is U*I*sin(phi), called the reactive power Q and measured in var. The three powers form a triangle:

 

"Some people die at 25 and aren't buried until 75." -Benjamin Franklin

 

What is life's greatest illusion?"  "Innocence, my brother." -Skyrim

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Looking at the photos online I am confident that it is a 630VA transformer and not a 2400VA unit. A 2400VA EI cored transformer is huge.

"This forum helps those that help themselves."

"If you think you need floating point to solve the problem then you don't understand the problem. If you really do need floating point then you have a problem you do not understand."

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Normally this type of transformer would be used for powering the control system, say for a large motor starter where you have 3 phase input. The primary is connected across two of the phases which is suggested by the primary voltages 440/460/480 which are used in North America and the secondary is 115/230 for your contactors etc.

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

pawi777 wrote:
P_N is the nominal power and P_K is the short circuit power (K for Kurzschluss). So it's a 630 VA Transformer that can draw up to 2.3 kVA when it's shorted. Verb. is short for Verbinden, meaning that these terminals should be connected together. Anschl. is short for Anschluss, meaning that's where you connect the power source (probably the grid) or the load respectively.

 

Thanks, it has been way to long since my HS German class!  

 

Jim

 

 

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

pawi777 wrote:

P_N is  the nominal power and P_K is the short circuit power (K for Kurzschluss). So it's a 630 VA Transformer that can draw up to 2.3 kVA when it's shorted.

Verb. is short for Verbinden, meaning that these terminals should be connected together.
Anschl. is short for Anschluss, meaning that's where you connect the power source (probably the grid) or the load respectively.

 

Thanks Pawi.  That's the info I was looking for.  Google translate did good on the Verb. and Anschl. since I was expecting to find something like "short/jumper" and "load/load connection".  I've located a couple of other transformers that look like better choices.  One is another German make, but it lists the amperage for the primary and secondary windings at each voltage as well as clearly stating it is a 2.4KVA transformer.

 

Thanks everyone for your help on this!

Cheers,

Tom

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Can you provide the specs on the servos? That's a lot of (dangerous) power to be dealing with.

Jim

If you want a career with a known path - become an undertaker. Dead people don't sue! - Kartman

Please Read: Code-of-Conduct

Atmel Studio6.2/AS7, DipTrace, Quartus, MPLAB user

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

I have four 40in-lb 180VDC motors that I'm powering.

Cheers,

Tom

  • 1
  • 2
  • 3
  • 4
  • 5
Total votes: 0

Do you have the specs on the motors?  Current requirements for example?  How many?

 